I had my garage built about 7 years ago by a contractor/handyman/good ol' boy, who also wired it.
In any case, all the outlets and lights and garage door openers have worked fine.
But recently I wanted to add a breaker for an outdoor outlet and I'm a bit stumped.
This is how the panel is wired:
Looks like he brought just one hot (black wire), one neutral (white wire) and a ground from our main panel via the upper left side punchout. Wired the hot to the 50A breaker screw at A. This is powering Bus D throughout the breaker. So the two 20A breakers work to supply everything via Bus D.
But the empty slots powered by Bus B provide nothing, having been hooked up to the neutral via terminal A.
Looks like he did it this way to provide a master breaker/cutoff.
Seems like the neutral should have gone to F for the neutrals and grounds, the hot to B and jumped to E (barely visible on the right) where a second hot wire would normally go. That would provide current to both busses, D & C. But with no master breaker.
Any thoughts? Is what's shown in the photo a common way to wire a breaker panel or just jury-rigged and wrong?
Thanks. I understand a bit about electricity and wiring but have not done very much with home wiring before.
In any case, all the outlets and lights and garage door openers have worked fine.
But recently I wanted to add a breaker for an outdoor outlet and I'm a bit stumped.
This is how the panel is wired:
Looks like he brought just one hot (black wire), one neutral (white wire) and a ground from our main panel via the upper left side punchout. Wired the hot to the 50A breaker screw at A. This is powering Bus D throughout the breaker. So the two 20A breakers work to supply everything via Bus D.
But the empty slots powered by Bus B provide nothing, having been hooked up to the neutral via terminal A.
Looks like he did it this way to provide a master breaker/cutoff.
Seems like the neutral should have gone to F for the neutrals and grounds, the hot to B and jumped to E (barely visible on the right) where a second hot wire would normally go. That would provide current to both busses, D & C. But with no master breaker.
Any thoughts? Is what's shown in the photo a common way to wire a breaker panel or just jury-rigged and wrong?
Thanks. I understand a bit about electricity and wiring but have not done very much with home wiring before.