I got the outside stuff done today:
I used 6-gauge THWN for the hots and common, and 10-gauge THWN for the ground (except in the box itself, which came with 6-gauge ground wires). I actually could have gotten away with 8-gauge THWN, but the cost difference was trivial and it gives me a bit of safety margin. It's a 50-amp circuit.
That's all I can do until the safety interlock comes in, which should be tomorrow. Then I can install the interlock, backfeed breaker, and inside wiring. I'll be using 6/3 Romex with ground for the interior wiring to the panel, mainly because I'm too lazy to run conduit. I also have to re-staple that coax I had to move.
Rich
I used 6-gauge THWN for the hots and common, and 10-gauge THWN for the ground (except in the box itself, which came with 6-gauge ground wires). I actually could have gotten away with 8-gauge THWN, but the cost difference was trivial and it gives me a bit of safety margin. It's a 50-amp circuit.
That's all I can do until the safety interlock comes in, which should be tomorrow. Then I can install the interlock, backfeed breaker, and inside wiring. I'll be using 6/3 Romex with ground for the interior wiring to the panel, mainly because I'm too lazy to run conduit. I also have to re-staple that coax I had to move.