Which generator is the correct minimum size for this welder
Generators - 105 selections
Which generator is the correct minimum size for this welder
Generators - 105 selections
Yes and budget is limited, the all-in-one will not work. ($)
Is it as simple as "200W output welder needs min 200W input"?
]Do you really mean a 2KW generator? ]
To find out the current drawn from the supply breaker, the arc voltage should be known and this is usually indicated in the specs plate of the equipment. If it says 40 volts, then your supply line and breaker should be higher than 30 amperes. If it is 30 volts, then a 30 amp supply breaker and line ampacity is just on the margin, 28 amps. If it is 50 volts, you really have to change your power supply line capacity to a little bit better than 50 amps. at full load of 225 amperes.
according to Lincoln Welder literature your model requires a 50amp input @ 230V single phase 60Hz at rated power.
http://content.lincolnelectric.com/pdfs/products/literature/e230.pdf
a 12KW generator would be just big enough, a 15KW unit would be better and relatively inexpensive
So this one is undersize?
according to Lincoln Welder literature your model requires a 50amp input @ 230V single phase 60Hz at rated power.
http://content.lincolnelectric.com/pdfs/products/literature/e230.pdf
She is going to half to rethink this, might be out of the budget.
Thanks for the input, you probably saved her some $
So this one is undersize?
She is mostly welding thick walled upset tubing for horse pens.
Yes she can get power from the mains for this project but there are other projects planned where it will be several hundred feet to any power supply......and she would like a self contained generator for other uses like running the fridge when the power fails.
A friend asked this.
Which generator is the correct minimum size for this welder
Generators - 105 selections
A friend asked this.
Which generator is the correct minimum size for this welder
Generators - 105 selections
The 225 number you mentioned is the current (amp) output of the welder and doesn't directly relate to the required current input.
That welder is expected to connect to a 50A 240v circuit which equates to 12KW. Typically devices attached to a 50A circuit average less than 40A but the peak input power could be as high as 60-75A (briefly). For that reason I'd go with something rated for 10KW continuous and 18KW surge (peak) as a minumum. That's a pretty big (and expensive) genset.