I have a ~dozen new shop LEDs to install; T8 x 8' and as is typical the (Chinese) manufacturer does not reveal the amp draw; best as I can tell they are going to be around a half amp each. 1A max.
My question is about the cable choice; it seems like way overkill to run 12awg to each lamp from the existing incandescent fixtures. (6' run for each. One lamp on each connection; no daisy chaining)
However if I use anything smaller, the cable will not have the protection which the CB is designed for.
(I'm interested in what code says although such things are not subject to code inspection where I live.) [I accept the legal ramifications of my choices, so let's press on to the practicalities]